Here is an attachment wherein (see box) the only requirement for running three phase motor on single phase supply is keeping the voltage across each winding of the three phase motor at its rated value and there is no requirement of de-rating mentioned in it.
kwired:
The problem with the ordinary static converters in
the market is the use of smaller size capacitor
with the result rated voltage does not appear ine
each winding of the motor and so it can not take
rated load. But if a capacitor of suitable size is
used as mentiod in my last POST, the motor can take
rated load on simglesimgle phase supply.
OK, these figures are from memory and could be slightly off but lets start with them.Thanks kwired for your reply. It would be moreinstructive if you supply numerical values for capacitors, motorrated current voltage etc you used so that I could check.:happyyes:
Sounds like a good theory, why did it not work that way when applied? BTW I believe the motor in my case was delta connected if that makes any difference.kwired:
There were two formulas given in the attachment of post#23-one for star connected motor and other for delta connected motor. The authors of that reference stated that to keep phase voltage of each winding of motor at its rated value during single phase operation, a capacitor of value approximately as given in the attachment is to be used. If what they stated to be true, then rated current would flow through each winding and so there would be no over load in any winding at the rated output of the motor. I tried to analyse the formula for star connection as below:
C=2800*In/V
C is in MFD. So for C in Farad,
C=2800*(In/V)*0.000001
For more accuracy, the factor 2800 is taken as 2745. So
C=2745*(In/V)*0.000001
2*3.14*f*C=2*3.14*f*2745*(In/V)*0.000001, where f=frequency=50Hz (mains frequency in Russia)
The reactance Xc of the capacitor =1/2*3.14*f*C. Therefore
Xc=(V/In)*1000000/2*3.14*50*2745=1.16*(V/In). So
In*Xc=1.16*V, the voltage across the capacitor.
As the rated current 'In' flows through the series motor phase winding, the voltage across it is 0.58*V. So the voltage across the capacitor and phase winding series combination is (1.16-0.58)*V=0.58*V,the voltage across the second phase winding of the motor. So this second motor phase winding would also take the rated current. It appears that the two currents would sum up to be double the rated current through the third phase winding of the motor. But that is not the case: the capacitor introduces necessary phase shift so that the vectorial sum of those two rated motor currents is equal to the rated current of the motor through the third winding.
Kind of what I ran into, I could get better balance by changing capacitor values, but the load in my case was not fixed and the balance changed as load changed. But no matter what load was or what capacitor value was being used I still had sum of two "phase leads" current on the third "phase lead", and when the motor was running at higher load the current in that one lead was well above motor namplate rating, up to 40 amps or so on a motor rated for somewhere around 25 amps.Kwired,
Good to see a "real world' response.
"""Sounds like a good theory, why did it not work that way when applied?"""
Have run across a similar application, and it worked only with a fixed load.
As you cautiously pointed out, there are more factors than included in the equations,
and that is where a good experienced Electrician has his merit.