M mravi New member Feb 15, 2005 #1 Is it permissible to convert a 3#3/0-11/2", 208V feeder to a 4#3/0, 120/208V, 3phase, 4 wire system to feed a power/lighting panel by just installing a neutral in separate conduit from the distribution panel source
Is it permissible to convert a 3#3/0-11/2", 208V feeder to a 4#3/0, 120/208V, 3phase, 4 wire system to feed a power/lighting panel by just installing a neutral in separate conduit from the distribution panel source