Am trying to arrive at 1ph amps needed. 10.1 kw @ 208 3ph, what amperage is needed at 240 1ph
Am trying to arrive at 1ph amps needed. 10.1 kw @ 208 3ph, what amperage is needed at 240 1ph
Well, a 10.1 kW load is a 10.1 kW load.Am trying to arrive at 1ph amps needed. 10.1 kw @ 208 3ph, what amperage is needed at 240 1ph
Am trying to arrive at 1ph amps needed. 10.1 kw @ 208 3ph, what amperage is needed at 240 1ph
Is this a motor or resistant heat or what?
The question does not make sense. If you have a single phase load, there is no way to connect it to a three phase power supply, and use all of the available wires. So what exactly are you trying to do with this oven? What do you mean by giving a power value at 208V 3 phase, if the load is single phase?10.1 kw @ 208 3ph, what amperage is needed at 240 1ph
See, that is part of the confusion here. I interpreted it the other way, that the equipment was rated at 240 and the available power source is 208. That is why we need clarification of the question.Plus since you are applying 240 instead of 208 volts you will get higher kW out of it unless . . . .
I am on board with that, for all we know we could both be wrong with what the application is.See, that is part of the confusion here. I interpreted it the other way, that the equipment was rated at 240 and the available power source is 208. That is why we need clarification of the question.
My apology for not being specific.Am trying to arrive at 1ph amps needed. 10.1 kw @ 208 3ph, what amperage is needed at 240 1ph
Can it be reconfigured to run on single phase? Some but not all of this type of equipment has that capability. That would be much simpler and less costly than adding phase conversion equipment, you possibly will still want to buck the voltage. Depending on what you have it may even cost less to find an oven with the right voltage/phases then to use phase conversion and buck transformers.My apology for not being specific.
This is a 3ph 208 oven that draws 10.1 KW according to its name plate. The power available is 1ph 240 volts. This will have to
have a buck and boost to bring the single phase to 208, and a phase inverter. What amperage will be needed
Thanks
The equipment is and oven rated at 10.1 kw 208 three phase. The supply is 240 single ph. This will probably have to be transformedSee, that is part of the confusion here. I interpreted it the other way, that the equipment was rated at 240 and the available power source is 208. That is why we need clarification of the question.
The equipment is and oven rated at 10.1 kw 208 three phase. The supply is 240 single ph. This will probably have to be transformed
to 208 single ph and phase converted. If the convertor pulls 7 amps how do i determine single ph ampere draw.