I am an electrical engineer and on one of my projects the electrician forgot to install a neutral from the secondary side of a buck boost transformer (240V-480V 1Phase) to the secondary fused disconnect switch. The distance between the transformer and the disconnect switch is approximately 1000ft. Wiring routed to the disconnect switch includes 2 hots & 1 ground wire( L1, L2 and G) . My question is: Can I use the ground wire as a neutral (as long as it appropriately sized per NEC Table 250.102 (C)(1)). The existing ground (green) wire will be reconnected to the neutral bus and labeled at each end as neutral. For the secondary disconnect switch grounding conductor, I am planning on running a new grounding electrode conductor from the ground lug of the disconnect switch to the counterpoise, installed at the secondary disconnect switch location, since it will be much cheaper than running a 1000ft of new wire and conduit.