How would you size the branch circuit (240 volts) using this info from the unit spec?

POWER / RATINGS

Amp Rating at 208V 50
Amp Rating at 240V 50
KW Rating at 208V 9.6
KW Rating at 240V 11.1
 
Note 4 of Table 220.55

4. Branch-Circuit Load. It shall be permissible to calculate the branch-circuit load for one range in accordance with Table 220.55. The branch-circuit load for one wall-mounted oven or one counter-mounted cooking unit shall be the nameplate rating of the appliance
 
Yes the table says that however the note to the table specifically states one oven at nameplate

Unless I'm not reading this correctly you need to differentiate between range and wall oven. The table applies to ranges according to the note #4 that you posted.

4. Branch-Circuit Load. It shall be permissible to calculate the branch-circuit load for one range in accordance with Table 220.55. The branch-circuit load for one wall-mounted oven or one counter-mounted cooking unit shall be the nameplate rating of the appliance
 
Yes, of course, you must differentiate between an oven and a range as they are not the same

A range is a cooktop with an oven. An oven is just an oven and a cooktop is just the burners. If you wire a cooktop and an oven then you can calculate the circuit as one range. For instance an 8kw cooktop and a 7 kw oven can be calculated to be the same as 1 - 15 kw range which would be 9.2kw.

Just an oven is the nameplate..
 
When applying note #4 (I've broken it down into three different sections) tell me if this looks correct:

Note #4. Branch-Circuit Load.
A) It shall be permissible to calculate the branch-circuit load for one range in accordance with Table 220.55.

B) The branch-circuit load for one wall-mounted oven or one counter-mounted cooking unit shall be the nameplate rating of the appliance.

C) The branch-circuit load for a counter-mounted cooking unit and not more than two wall-mounted ovens, all supplied from a single branch circuit and located in the same room, shall be calculated by adding the nameplate rating of the individual appliances and treating this total as equivalent to one range.

A) Use the kW rating of the range with T220.55.
B) Use the kW rating for the wall-mounted oven or counter-mounted cooking unit.
C) Use the kW rating of the counter-mounted cooking unit and wall-mounted oven added together and T220.55 as if it were a single range.

I mention this (using only the kW ratings) because if you look at the spec in post #1 you'll see different kW ratings but the same 50 amp rating for both voltages.
 
Your analysis is correct Trevor.

If you divide the kw's by the perspective voltages they both come in at 46 amps so a 50 amp is appropriate using either voltage.
 
Note 4 applies to the branch circuit. For a single oven or single cook top - you must use appliance rating for the branch circuit, but can use the table for demand rating to apply to a feeder or service. Now throw in a feeder that only supplies the one branch circuit....:blink:
 