While troubleshooting a no start on a diesel generator for my company I found 2 volts from the main cable feed to starter from 12 volt battery source to ground.
I suspected a ground issue since battery was fully charged. Also nothing on generator worked and when I jumped both positive and ground jumper cable direct to starter it still spun slow.
Sure enough I found a bad negative connection clear the hell down almost to negative post so you got 12 volts showing almost at negative terminal. Something you don’t see often but text books always mention
Cut off bad, worn out carbon tracked corroded end and cleaned up all grounds and problem solved.
Another project I had similar to this was a tractor drill that had its ground completely disconnected and voltage Positive 12v showing on chassis relative to battery negative
I suspected a ground issue since battery was fully charged. Also nothing on generator worked and when I jumped both positive and ground jumper cable direct to starter it still spun slow.
Sure enough I found a bad negative connection clear the hell down almost to negative post so you got 12 volts showing almost at negative terminal. Something you don’t see often but text books always mention
Cut off bad, worn out carbon tracked corroded end and cleaned up all grounds and problem solved.
Another project I had similar to this was a tractor drill that had its ground completely disconnected and voltage Positive 12v showing on chassis relative to battery negative