Coomercial Kitchen GFCI Recptacles

Status
Not open for further replies.

Riograndeelectric

Senior Member
commercial kitchens GFCI Oultets. Article 210.8.B lists that all 125V single pahse 15/20 amp recps in Commercial and Institutional shall have GFCI protection.

I had a call where the GFCI oultets had been tripping and it was not due to any ground faults but rather the heating elements creating havic on the GFCI.
Has any on thought about using a 30ma GFP Breaker instead of the normal 5ma GFCI.
 
Riograndeelectric said:
I had a call where the GFCI oultets had been tripping and it was not due to any ground faults but rather the heating elements creating havic on the GFCI.

That is a ground fault, have them replace the heating elements.

Has any on thought about using a 30ma GFP Breaker instead of the normal 5ma GFCI.

You can not use a GFP breaker for personal protection.
 
Riograndeelectric said:
I had a call where the GFCI oultets had been tripping and it was not due to any ground faults but rather the heating elements creating havic on the GFCI.
.
You absolutely need a megger to troubleshoot these nuisance GFCI tripping service calls. There's nothing fundamental about a heating element that will trip a GFCI. A failing (faulted or faulting) heating element will trip them. A megger will prove that out in short order. I find a megger to be an essential tool when troubleshooting intermittant GFCI and AFCI tripping issues.
 
We have heating elements in some of our machines that will occasionally blow fuses. You check the heaters and everything is fine, 2 days later same fuse blows again. Come to find out when they are heating/hot they can occasionally move and short out to ground.
 
Status
Not open for further replies.
Top