Copper clad steel isn’t mentioned and therefore not allowed in the NEC IMOI am not familiar with what the NESC says about copper clad steel however I’m guessing that the NEC won’t approve this due to a life span of 40-50
Unless it is listed maybe?Copper clad steel isn’t mentioned and therefore not allowed in the NEC IMO
250.62Grounding Electrode Conductor Material. The grounding electrode conductor shall be of copper, aluminum, copper-clad aluminum, or the items as permitted in 250.68(C). The material selected shall be resistant to any corrosive condi‐ tion existing at the installation or shall be protected against corrosion. Conductors of the wire type shall be solid or stran‐ ded, insulated, covered, or bare.Unless it is listed maybe?
We started using it to stop (or lessen) copper theft.Curious. I had to look up copper clad steel wire to see what it even is. Apparently One of its primary uses is in grounding systems.
Maybe the utility has started using it so the electrical contractor figured if it was good enough for the utility is good enough for him.
Maybe figures inspector won't notice any difference and he cuts costs with it.Curious. I had to look up copper clad steel wire to see what it even is. Apparently One of its primary uses is in grounding systems.
Maybe the utility has started using it so the electrical contractor figured if it was good enough for the utility is good enough for him.
not sure what the point is. #6 copper can't be all that much more expensive than this stuff.Maybe figures inspector won't notice any difference and he cuts costs with it.
simple to check with a magnet to tell if it has steel in it though.
Most tracer wire I've seen is only like 12 AWG size or something close to it and is usually covered and not bare.not sure what the point is. #6 copper can't be all that much more expensive than this stuff.
I poked around the Internet and found it is also used as a tracer wire so underground utility installations can be tracked down.
I did not look real close at it.Most tracer wire I've seen is only like 12 AWG size or something close to it and is usually covered and not bare.
It is just a gec.#6 copper clad steel is definitely is not electrically equivalent to #6 copper. Even if it was acceptable to use per the NEC I'm guessing you would need to use a much larger conductor.
So the sizing specified by the NEC for copper, aluminum and copper-clad aluminum can be ignored?It is just a gec
The code does not specify a size for copper clad.So the sizing specified by the NEC for copper, aluminum and copper-clad aluminum can be ignored?
Look at Table 250.66. It states sizes for copper-clad aluminum. Aluminum is a better conductor that steel so who know what the equivalent size of copper-clad steel would be.The code does not specify a size for copper clad.
Think of it this way. If it is connected to a rod the rod might we'll be made of steel. Logically, Why can the rod be steel but not the conductor?
The rods are supposed to have at least 10 mils of cladding on a 5/8 rod which is SUPPOSED to be equal to a #6 copper rod.The code does not specify a size for copper clad.
Think of it this way. If it is connected to a rod the rod might we'll be made of steel. Logically, Why can the rod be steel but not the conductor?