Ground Loop Guru
- Oxnard, CA
I teach AC Power and Grounding to students in the recording studio, home theater, and sound reinforcement industries. I'm an electronics engineer (analog circuit design) ... not an electrician, so I apologize up front if my terminology is unfamiliar. I will be teaching at an Audio Engineering Society regional meeting in Toronto next month. I'll be sharing the stage with a representative of a company that makes 120 VAC Isolation Transformers - of the same kind discussed in a June-July 2008 thread called "Isolation Transformer Grounding". I've maintained for years that the outlets on these devices must have their EGC connected to both the enclosure and to the incoming power (via cord and plug) EGC ("safety ground" as I most often refer to it. They claim their products eliminate that connection between incoming and outgoing EGC, so I expect I'll be taken to task to justify my objection. It's not a so-called "balanced power" unit that can use GFCIs at the output to comply with code.
All that being said, I believe there was a NEC section that specifically prohibited disconnection of the link tying input EGC to output (outlet) EGC. I used to have the reference (to NEC 2008 if memory serves) in one of my PowerPoint slides. But recent hacking into my computers has wiped virtually all of my reference material (a very sad story in itself but I'll spare everyone). My question to the forum is: Can anyone supply me with the NEC citation - to a current edition of code, if possible?
Bill Whitlock
Whitlock Consulting
Oxnard, CA
Bill Whitlock
Whitlock Consulting
Oxnard, CA