Why does the NEC limit cord and plug connected equipment to 80% of the receptacle's/cord cap rating? Is there anyway to legally draw 100%?
(1) Not sure, but the requirement only applies to branch circuits supplying two or more outlets, (2014) 210.21(B)(2). They want to leave 20% for other hardwired loads? E.g. mixing lighting and receptacles?Why does the NEC limit cord and plug connected equipment to 80% of the receptacle's/cord cap rating? Is there anyway to legally draw 100%?
What code section are you referring to?Why does the NEC limit cord and plug connected equipment to 80% of the receptacle's/cord cap rating? Is there anyway to legally draw 100%?
I wasn't sure if he was referring to a circuit with 2 or more receptacles or a single receptacle. The OP seems to be focusing on the cord.He's referring to 210.21(B)(2) which is a stupid code section / Table anyways. What the end user does after the CO can not be controlled by an AHJ or inspector.