Cord and plug HVAC, Wet location, Ground Fault protection
CherokeeXJ
North Carolina
Licensed Electrician
A cord and molded plug window hvac unit is going in a greenhouse for temperature control. The plug has a ground fault device similar to a hair dryer with a test and reset button.
It will need a 20 amp 240 volt receptacle to run on.
This being a wet location I will be installing a weatherproof box and weatherproof in-use cover and that brings me to the question of ground fault protection.
Ground fault protection is needed for a receptacle in a wet location, but has anybody had experience with how a window hvac unit and ground fault breaker agree?
It’s a $150 breaker and I don’t want to buy it to find out the breaker trips on start up. Thanks for any help or suggestions.
I Have no idea. It shouldn't trip initially but my concern is a window A/C being used in a wet location. The outside obviously can get wet, but the controls on the inside aren't intended to. I suspect that water and moisture in the inside half will cause leakage and trip the breaker.
-Hal
I didn’t think about it that way, but a ground fault device actually on the plug end should remedy that no matter where it’s installed which is similar to the plug end of a hair dryer for example. So I would think it would be acceptable in any “indoor” location, but I will definitely look in the manufacturers instructions on that.
You can be indoors, but be in a wet location.
I’ll be checking on the environment the unit can be exposed to, but it does have a ground fault device on the cord end like a hair dryer does.
My original question was has anyone had experience with running a window hvac unit that is cord and plug connected in conjunction with a gfci breaker?
Under normal circumstances there would be no problem. I have installed GFCI receptacles for a hot tub that had GFCI on the cord. No problems with it.
Let's clear this up. The A/C plug is not a GFCI. It called an LCDI and only protects against damaged cords. We've discussed this before:
-Hal