benaround said:
That's the I read it also.

It's a pendent, 400.7(A)(1). Pendents do not require male cord caps.


Very common in food service areas, take look behind the counter at the local Micky Ds. :smile:
 
iwire said:
It's a pendent, 400.7(A)(1). Pendents do not require male cord caps.


Very common in food service areas, take look behind the counter at the local Micky Ds. :smile:

Bob,

I'm going to back off on this one, IMO, it is poorly put together (400.7(A) )

For example: if you have a pendant recpt. can you use it for ( 400.7A(6) )

connection of equipment to faclitate frequent interchange, without 400.7B

coming into the picture?
 