I found an unusual condition. The cord grips that support a 4/0 SOOW DLO single-conductor cord feeding a tap box are getting hot, but the SOOW Cords are not hot to the touch. I'm assuming an induced voltage causes this. What are your thoughts?
300.20(B) talks about that method, but the cord grips would have to be nonferrous for that to work.An 'old' trick was to cut a slit in the enclosure between the conduits.
Assuming it didn't need to be NEMA 12 or 4...An 'old' trick was to cut a slit in the enclosure between the conduits.
Otherwise they bridge the gap that you just created...300.20(B) talks about that method, but the cord grips would have to be nonferrous for that to work.
How hot is "hot"? In general the inductive reactance heating is not a real issue until you have 300-400 amps of current.
Even though the manufacturer's tables will often show that conductor at 405 amps, that is in free air and at 90°C....very unlikely you are permitted to use the cable at that ampacity for any NEC application. There may be some applications where you could use it at 380 amps, but for most NEC applications, you will be limited to 230 amps, and that should not result in excessive heating where a single conductor is run through ferrous metal.
Note that both the enclosure and the cord grip, if made of ferrous materials will contribute to the inductive heating.
It is hot enough that I have to let go after 3 seconds.How hot is "hot"? In general the inductive reactance heating is not a real issue until you have 300-400 amps of current.
Even though the manufacturer's tables will often show that conductor at 405 amps, that is in free air and at 90°C....very unlikely you are permitted to use the cable at that ampacity for any NEC application. There may be some applications where you could use it at 380 amps, but for most NEC applications, you will be limited to 230 amps, and that should not result in excessive heating where a single conductor is run through ferrous metal.
Note that both the enclosure and the cord grip, if made of ferrous materials will contribute to the inductive heating.
How much current is flowing on the conductors?It is hot enough that I have to let go after 3 seconds.