mark32
Senior Member
- Location
- Currently in NJ
An old timer came into HD today and had some #8 solid cut for himself, then asked me for an FS box w/two entry's so he could run run his bond into it. I asked him why and his plan was to install his twist lock, for the pool pump, in the box then wire nut the equipment ground to the #8. Inside I started laughing but we began discussing the code which he seemed knowledgeable but I had to admit to him that it is not the intend of the code for him to do that and also, his idea was one I've never heard of or saw. His thinking is that if one were to unplug the pump, there would no longer be an equipment ground and bond connection at the pump. After he left it dawned on me that he maybe onto something. It is possible that if the pump were unplugged, there could be a difference in potential between the pump housing and the metal box the twist lock is mounted in. Does this makes sense?