lpalmer
Member
- Location
- California
I understand that cords are not allowed to be located above suspended ceilings, per 2005 NEC Section 400.8(5).
However, Section 300.23 indicates that suspended ceiling panels are allowed to be used to access equipment.
And given that Article 400.7(A)(8) states: Cords may be used for appliances.
And given that Article 400.8 states: Unless specifically permitted in 400.7, flexible cords and cables shall not be used in the following: (5) where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings. And Section 400.7 specifically allows use of cords for appliances. I do not see where the NEC restricts the use of cord equipped appliances above a suspended ceiling.
The area above suspended ceiling used for environmental air, would be a questionable location for a cord equipped appliance: However, wouldn’t the cord equipped appliance be acceptable if it met the requirements of 300.22(C)(2)?
If it's really the intent that cord equipped appliances are not permitted above a suspended ceiling, then shouldn't the NEC disallow receptacles in the same location and clarify the rules?
However, Section 300.23 indicates that suspended ceiling panels are allowed to be used to access equipment.
And given that Article 400.7(A)(8) states: Cords may be used for appliances.
And given that Article 400.8 states: Unless specifically permitted in 400.7, flexible cords and cables shall not be used in the following: (5) where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings. And Section 400.7 specifically allows use of cords for appliances. I do not see where the NEC restricts the use of cord equipped appliances above a suspended ceiling.
The area above suspended ceiling used for environmental air, would be a questionable location for a cord equipped appliance: However, wouldn’t the cord equipped appliance be acceptable if it met the requirements of 300.22(C)(2)?
If it's really the intent that cord equipped appliances are not permitted above a suspended ceiling, then shouldn't the NEC disallow receptacles in the same location and clarify the rules?
Last edited: