i had a service call last week at a mall parking lot. There was a 120/208 wye/ 480 delta transformer feeding a lighting panel. In this case the delta was the load and the Wye was the line side. the problem is the C phase on the wye side is pulling ov 200 amps and the others almost nothing. I did notice there was no corner ground on the delat side and a neutral was connected in the Wye side. I dont have a lot of experience with delta systems,so I apologize if this is a dumb question.... but it seems to me that there is a ground fault on one phase only so it is not tripping a breaker.
If corner ground the delta side and remove the jumper from xo to ground on the wye side would that at least show me where the fault is?
Any advice?
thanks
If corner ground the delta side and remove the jumper from xo to ground on the wye side would that at least show me where the fault is?
Any advice?
thanks