Yes, but the breakers have to be rated 240 and not 120/240. The grounded conductor still has to be in compliance with Article 200.Can i use a service panel with a three pole main breaker. for a corner grounded delta?
Because all conductors will open simultaneously.HOW can it be complaint with article 200 when the grounded conductor is landed on a over current device .