brian john
Senior Member
- Location
- Leesburg, VA
the chance of getting shocked is slim
AHHH but get between the ground and a phase (other than the grounded conductor/phase) and the potential is higher that in a properly installed Wye.
the chance of getting shocked is slim
Well, due to the lack of a solid ground connection, there is certainly the potential for a higher-than-secondary potential due to either induction or internal/external primary-to-secondary faults.brian john said:AHHH but get between the ground and a phase (other than the grounded conductor/phase) and the potential is higher that in a properly installed Wye.
brian john said:AHHH but get between the ground and a phase (other than the grounded conductor/phase) and the potential is higher that in a properly installed Wye.
Thanks again for all the insight, especially winnie, rattus and brian. Please allow me to summarize my thoughts on this corner grounded topic. First, if one phase is intentionally grounded the load will still see this as a three phase supply. Secondly, if one were to touch an enclosure that was bonded with said grounded conductor, the chance of getting shocked is slim because the equipment's potential is very low because it is bonded to the frame of the transformer, ges, and connected to one of the transformer's windings and will open the ocpd when one of the ungrounded conductors shorts to ground. Thirdly, in an ungrounded system, one should not get shocked by touching properly grounded equipment that contains a single fault because it's potential is also kept low due to being bonded, via the equipment ground, to the frame of the transformer and grounding electrode system. However, because there is no connection to the source the ocpd will only open when a second fault occurs. Is what I have stated above correct?
brian john said:FROM mark32
I just took this thought to the next level
mark32 said:I got ya rattus, what I meant by "Getting shocked is slim" is the theory that if one touches an enclosure/equipment that was bonded by the grounded conductor, that which in this case also feeds a motor, that the person should not get shocked if they were to find themselves between another piece of grounded equipment and said enclosure. Certainly, getting between a hot and this grounded phase could ruin one's day.
Um, Ben Franklin, while holding a kite string?rattus said:Who said, "The risk of getting shocked is slim"?