Need a double check on corner grounded 240V Delta:
Our new building came with a 240V corner grounded delta service. There seems to be lots of confusion on the part of the EC regarding proper hookup of transformers to a corner grounded Delta service.
We several have transformers that are 240V Delta -----> 208/120V Wye to serve convenience receptacles and office loads. I believe these are connected correctly, but will have to check.
We have several step-up trafos to supply some of our machine tools with 480V three phase (240V Delta -----> 480V Wye), and this is where I believe the EC is incorrect in his installation and connections:
1) He has run a #6 green from the transformer chassis back to building steel, but has also bonded the grounded leg of the three phase supply to the transformer chassis. I'm of two minds on this; I know this potentially creates multiple paths to ground (ground loops) but this is a very old building, and the portion of the building housing the transformer may or may not have continuous building steel back to the service entrance (we can't really tell). On the other hand, tying the grounded leg to the transformer chassis ensures a fault clearing path back to the service. Thoughts?
2) He has not tied H0 (the center point of the 480V Wye) to ground in the transformer. He says you don't do that. I say you need to in order to give the 480V side a ground reference and a fault clearing path. An ungrounded delta supply would need ground detectors, and could be the reason for damage the connected electronic control unit of the compressor unit being powered by this trafo. Thoughts?
Also, at our paint booth:
3) Our paint booth has (2) separate supplies. A 100A, 240V corner grounded Delta three phase supply needed to power the large VFDs for ventilation fans, as well as a 30A, 120V single phase supply (fed from a separate 208/120V panel) to separately feed control needs and lighting (this thing is rather strangely designed). He has tied the grounded phase of the delta supply to the green lug in the control panel, and has not run a separate ground conductor from the three phase service. Since the supply runs through nonmetallic conduit for part of its run, I say an appropriately sized ground conductor is needed; you don't get "credit" for grounding the machine through the grounded phase, correct?
3a) The 30A 120V single phase supply has no ground conductor run with it either (also through a section of nonmetallic conduit). Each feed to the machine must have an appropriately sized ground conductor back to it's supply for fault clearing, yes? You can't rely on the 3-phase supply to ground the single phase supply, yes?
Corner grounded Delta is a strange beast to many people these days, since it isn't commonly installed anymore. Thanks for the help!
SceneryDriver
Our new building came with a 240V corner grounded delta service. There seems to be lots of confusion on the part of the EC regarding proper hookup of transformers to a corner grounded Delta service.
We several have transformers that are 240V Delta -----> 208/120V Wye to serve convenience receptacles and office loads. I believe these are connected correctly, but will have to check.
We have several step-up trafos to supply some of our machine tools with 480V three phase (240V Delta -----> 480V Wye), and this is where I believe the EC is incorrect in his installation and connections:
1) He has run a #6 green from the transformer chassis back to building steel, but has also bonded the grounded leg of the three phase supply to the transformer chassis. I'm of two minds on this; I know this potentially creates multiple paths to ground (ground loops) but this is a very old building, and the portion of the building housing the transformer may or may not have continuous building steel back to the service entrance (we can't really tell). On the other hand, tying the grounded leg to the transformer chassis ensures a fault clearing path back to the service. Thoughts?
2) He has not tied H0 (the center point of the 480V Wye) to ground in the transformer. He says you don't do that. I say you need to in order to give the 480V side a ground reference and a fault clearing path. An ungrounded delta supply would need ground detectors, and could be the reason for damage the connected electronic control unit of the compressor unit being powered by this trafo. Thoughts?
Also, at our paint booth:
3) Our paint booth has (2) separate supplies. A 100A, 240V corner grounded Delta three phase supply needed to power the large VFDs for ventilation fans, as well as a 30A, 120V single phase supply (fed from a separate 208/120V panel) to separately feed control needs and lighting (this thing is rather strangely designed). He has tied the grounded phase of the delta supply to the green lug in the control panel, and has not run a separate ground conductor from the three phase service. Since the supply runs through nonmetallic conduit for part of its run, I say an appropriately sized ground conductor is needed; you don't get "credit" for grounding the machine through the grounded phase, correct?
3a) The 30A 120V single phase supply has no ground conductor run with it either (also through a section of nonmetallic conduit). Each feed to the machine must have an appropriately sized ground conductor back to it's supply for fault clearing, yes? You can't rely on the 3-phase supply to ground the single phase supply, yes?
Corner grounded Delta is a strange beast to many people these days, since it isn't commonly installed anymore. Thanks for the help!