Can someone help me understand the code requirement of 240.22. I just can't understand what it is saying. If you have the mike holt dvd "Transformer Calculations" from 2014 its discussed at the 15:00 minute mark in the bonus material section "grounded and ungrounded systems"
240.22 Grounded Conductor
No overcurrent device shall be connected in series with any conductor that is intentionally grounded, unless one of the following two conditions is met:
1. The overcurrent device opens all conductors of the circuit, including the grounded conductor, and is designed so that no pole can operate independently.
2.Where required by 430.36 or 430.37 for motor overload protection.
They are talking about terminating the ungrounded conductor in a 3 phase disconnect on one of the lugs and installing a bar in between. Or a 3 pole CB where one of the phases will be white....