bradp
Member
- Location
- Dallas, Texas
We have a code comment regarding applying article 220.12 to a branch circuit panelboard in a parking garage. It looks like it a canned plan review comment. Upon calling the city, the plans examiner who answered the phone (but did not make the comment) said it was a standard comment.
This has caused debate in our office regarding the application of NEC Table 220.12. I apply this table to a service calculation, and use the connected lighting load at 125% for branch circuit panelboard calculations. I think what is confusing the issue is that 220.12 is listed under branch-circuit load calculations.
Some are saying that 220.12 needs to be applied to a standard 1P-20A lighting circuit (although never done in our office)
Some are saying that the feeder to the parking garage panel should take NEC 220.12 into account
Some are saying that the service calculations should reflect NEC 220.12
What is the correct application of this code section? In my opinion NEC 220.12 is applied at a service calculation. I think this is backed up by the change in the 2014 code that allows the exception as follows:
Lighting loads are now permitted to be calculated at values specified in an applicable energy code where it is adopted by the jurisdiction. Three conditions of the new exception include monitoring, alarms and not applying demand factors to the general lighting load as provided in 220.42.
Thanks in advance for any responses.
This has caused debate in our office regarding the application of NEC Table 220.12. I apply this table to a service calculation, and use the connected lighting load at 125% for branch circuit panelboard calculations. I think what is confusing the issue is that 220.12 is listed under branch-circuit load calculations.
Some are saying that 220.12 needs to be applied to a standard 1P-20A lighting circuit (although never done in our office)
Some are saying that the feeder to the parking garage panel should take NEC 220.12 into account
Some are saying that the service calculations should reflect NEC 220.12
What is the correct application of this code section? In my opinion NEC 220.12 is applied at a service calculation. I think this is backed up by the change in the 2014 code that allows the exception as follows:
Lighting loads are now permitted to be calculated at values specified in an applicable energy code where it is adopted by the jurisdiction. Three conditions of the new exception include monitoring, alarms and not applying demand factors to the general lighting load as provided in 220.42.
Thanks in advance for any responses.