I posted something like this back in 2001, and never really got it cleared up. I'd like to see if there are any new products anyone can recommend:
Around here (Los Angeles), the usual residential service is 3-wire #1 with the GEC run in #6 CU solid armored or #4 CU solid bare. The electodes for most older and some new construction are the water service pipe and a 5/8" x 8' driven rod.
If you use the armored #6 GEC:
The armor has to be bonded at both ends. There are water pipe ground clamps with lugs for the armor as well as the conductor like the Burndy C11JA or C6D, and we sometimes use these for ground rod connections (with the clamp reversed to make a tight connection) or we just mash the armor into an acorn clamp. At the LC, we use a 3/8" MC connector or an Rx clamp on the armor (with a grounding bushing if it's in a multiple KO).
For the #4 w/o armor:
We use an Rx clamp at the box or just run the conductor through a small hole provided for that purpose (I think). There's no problem finding listed clamps for the groumd rod or water pipe electrode in this case.
I haven't had trouble getting AHJ approval with any of the above, but it still bothers me that I don't really know the correct listed connectors to use for the GEC on the most common residential service. So, what connectors would YOU use for:
1. #4 Solid CU GEC to LC
2. #6 Solid CU Armored GEC to LC
3. #6 Solid CU Armored GEC to Ground Rod
BTW, the whole armored GEC application bothers me because the 8' rod is supposed to be completely buried, but then the connector has to be approved/listed for burial (which the Burndy C6D is) but the armor itself isn't as far as I know. In fact, the armor rapidly degrades when it's in contact with soil even in dry Los Angeles. So, we generally don't drive the rod all the way, which is possibly the lesser of two evils.
A lot simpler to run the GEC in rigid or IMC, at least I'd know what fittings to use - but of course it would be too expensive...
Around here (Los Angeles), the usual residential service is 3-wire #1 with the GEC run in #6 CU solid armored or #4 CU solid bare. The electodes for most older and some new construction are the water service pipe and a 5/8" x 8' driven rod.
If you use the armored #6 GEC:
The armor has to be bonded at both ends. There are water pipe ground clamps with lugs for the armor as well as the conductor like the Burndy C11JA or C6D, and we sometimes use these for ground rod connections (with the clamp reversed to make a tight connection) or we just mash the armor into an acorn clamp. At the LC, we use a 3/8" MC connector or an Rx clamp on the armor (with a grounding bushing if it's in a multiple KO).
For the #4 w/o armor:
We use an Rx clamp at the box or just run the conductor through a small hole provided for that purpose (I think). There's no problem finding listed clamps for the groumd rod or water pipe electrode in this case.
I haven't had trouble getting AHJ approval with any of the above, but it still bothers me that I don't really know the correct listed connectors to use for the GEC on the most common residential service. So, what connectors would YOU use for:
1. #4 Solid CU GEC to LC
2. #6 Solid CU Armored GEC to LC
3. #6 Solid CU Armored GEC to Ground Rod
BTW, the whole armored GEC application bothers me because the 8' rod is supposed to be completely buried, but then the connector has to be approved/listed for burial (which the Burndy C6D is) but the armor itself isn't as far as I know. In fact, the armor rapidly degrades when it's in contact with soil even in dry Los Angeles. So, we generally don't drive the rod all the way, which is possibly the lesser of two evils.
A lot simpler to run the GEC in rigid or IMC, at least I'd know what fittings to use - but of course it would be too expensive...