kreed
Member
- Location
- Michigan City
- Occupation
- Electrician
I am installing a standby automatic generator on on a 240v 3phase delta grounded b phase service. This is the first time I have installed a generator on a system with this configuration. I have a couple questions and concerns. Looking for some confirmation and/or direction. First off, as all of the service conductors will not be connected at any point between the utility and generator, I see the generator as a separately derived service. This would require me to install a grounding electrode and a GEC. I am told I will just need to literally connect a conductor from b phase to a grounding electrode(ground rod). One concern is the bonding between the grounded b phase and the GEC. Can the conductor that grounds b phase also serve as the GEC? If so, how does the bonding work in the transfer switch? I feel like the b phase to ground and the GEC need to be separated with the GEC having an independent conductor from its own electrode to the transfer switch. And bonding the frame of the generator as well. No where in the utility service is b phase bonded to the grounding system of the service. B phase is grounded at the transformer and the service is grounded at the service. I believe this is the correct way to install the grounding. No bond to b phase at the service disconnect. If all this is correct, I don't believe there is a required distance between the two different electrodes. So it should be the same for the generator. Am I making this more complicated than it needs to be? Grounded b phase always gets the brain smoking!