amluto
Member
- Location
- San Mateo County, California
My in-progress electrical service has an outdoor meter box and an indoor main panel and service disconnecting means. The AHJ is okay with the location of the service disconnecting means but requires an outdoor device that responders can use to turn off power without entering the building.
NEC 230.70 seems to allow remotely operated breakers, and it seems like the intent is to have a remote button or switch that trips the main disconnect, so long as the main disconnect can also be manually operated. The details are unclear to me, though. What is the correct way to configure a shunt trip device? I assume we can power it from the load side of the main breaker, but does it require its own overcurrent protection? If so, can that be a small breaker in the main panel (in which case the shunt trip will not operate if that breaker is turned off), or should it be a separate fuse?
NEC 230.70 seems to allow remotely operated breakers, and it seems like the intent is to have a remote button or switch that trips the main disconnect, so long as the main disconnect can also be manually operated. The details are unclear to me, though. What is the correct way to configure a shunt trip device? I assume we can power it from the load side of the main breaker, but does it require its own overcurrent protection? If so, can that be a small breaker in the main panel (in which case the shunt trip will not operate if that breaker is turned off), or should it be a separate fuse?