your in a bad spot. don't cut corners. fix it. Sorry. Too much liability
moo2380 said:That makes absolute sense, even though the code allows for this installation (i.e. skewed EMT connectors) “tight”.
Although he would have to produce from the MFG the listing of the connector which would have to indicate the proper installation of the connector as it’s designed.
Pierre C Belarge said:Why is that so?
Think "effective ground fault current path" as per 250.4(A)(5)
moo2380 said:That makes absolute sense, even though the code allows for this installation (i.e. skewed EMT connectors) ?tight?.
However if the Inspector wanted to push the issue he probably could call it a violation of 110.3 incorrect installation according to the listing and labeling..?? Although he would have to produce from the MFG the listing of the connector which would have to indicate the proper installation of the connector as it?s designed.
I?m probably going to lose this one, but since the explanation of the test criteria surrounding UL 514B this makes sense.
moo2380 said:The conduit run is for a 1200A feeder circuit, I under bent the 90 and tightened down on the locknut but cabinet wouldn?t conform to the EMT connector, big money to change now. My thoughts are that as long as the EMT connectors locknut was in contact with a couple of the ?tabs? from the locknut and the it?s tight, than it would be ok. The Inspector couldn?t support his claim with a ?listing? of the product which might defend his position on the ?correct? installation, so then as long as the connector is ?tight? then why wouldn?t it be able to clear a fault. I think that maybe the Inspector might be a little ?Nit Picky?, or maybe I missed something to be fair, I?m not sure.?
As far as testing the equipment, is there a standard that dictates an EMT connectors grounding performance when installed with partial surface contact or full surface contact as long as the contact is "tight"?
Article: 110.12 Mechanical Execution of Work
Electrical equipment shall be installed in a Neat and Work- Manlike manner.!
hey. Relax. It's not the end of the world.The issue isn't correct installation of EMT connectors, if the conduit was bent properly the lock nut would be seated correctly.
Article: 110.12 Mechanical Execution of Work
Electrical equipment shall be installed in a Neat and Work- Manlike manner.
Since you didn't provide any pictures, and the electrical inspector didn't approve the installation, the conduit in question must look shoddy at best.
Since you are working with larger conduit and wire, the time to correct the problem was before you pulled the wire.
Next time take some PRIDE in your installation!
Talk to the inspector and explain calmly and politely about the extensive amount of work involved and the associated costs of redoing the poorly bent conduit. Then admit your wrong to him and ask if he will allow you to use bonding locknuts with the wire sized according to 250.66 if it's the service entrance conductors or 250.122 if it's an equipment ground.
Admitting your fault and asking for his "help" in fixing your screw up might just get you out of this mess with the least amount of physical work and costs.
Sometimes we must swallow our pride and eat some crow