I am designing an Administration Building, which is an Occupancy Type B. In that building I am trying to determine how to correctly interpret Article 210.65 of the 2022 California Electrical Code. My question pertains to the layout of the outlets within a 512sqft conference room in this building. Article 210.65 states the following:
Each meeting room of not more than 93 m2 (1000 ft2) in other than dwelling units shall have outlets for nonlocking-type, 125-volt, 15- or 20-ampere receptacles. The outlets shall be installed in accordance with 210.65(B). Where a room or space is provided with movable partition(s), each room size shall be determined with the partition in the position that results in the smallest size meeting room.
This room does not have any movable partitions so I think we can ignore the second sentence. The first sentence refers me to 210.65(B), which states:
The total number of receptacle outlets, including floor outlets and receptacle outlets in fixed furniture, shall not be less than as determined in (1) and (2).
In other words, 210.65 points me right back to 210.52(A)(1)-(A)(4), which lists the requirements for outlets in Dwelling Units, i.e. one every 12ft (one outlet within 6ft of any position along the wall), etc etc. Am I interpreting this correctly? Do I need to install receptacles in this conference room as I do in dwelling units?
Each meeting room of not more than 93 m2 (1000 ft2) in other than dwelling units shall have outlets for nonlocking-type, 125-volt, 15- or 20-ampere receptacles. The outlets shall be installed in accordance with 210.65(B). Where a room or space is provided with movable partition(s), each room size shall be determined with the partition in the position that results in the smallest size meeting room.
This room does not have any movable partitions so I think we can ignore the second sentence. The first sentence refers me to 210.65(B), which states:
The total number of receptacle outlets, including floor outlets and receptacle outlets in fixed furniture, shall not be less than as determined in (1) and (2).
(1) Receptacle Outlets in Fixed Walls
The required number of receptacle outlets shall be determined in accordance with 210.52(A)(1) through (A)(4). These receptacle outlets shall be permitted to be located as determined by the installer, designer, or building owner.In other words, 210.65 points me right back to 210.52(A)(1)-(A)(4), which lists the requirements for outlets in Dwelling Units, i.e. one every 12ft (one outlet within 6ft of any position along the wall), etc etc. Am I interpreting this correctly? Do I need to install receptacles in this conference room as I do in dwelling units?