I have a 40hp 480V motor with a FLA rating of 47A. The only overload that I have avaliable is an electronic adjustable type with the lowest setting being 64A. I want to run this motor ASAP however I am concerned that the lowest setting of 64A on the overload will be too high to protect the motor adequately. I know in the code it allows sizing of the overloads to be 125% FLA and even sized up to 140% FLA for some cases. The 64A setting will give me a value of 136% of full load for this motor.
Will this setting work for this motor or will I possibly have problems down the road. The motor is a NEMA B type motor.
Will this setting work for this motor or will I possibly have problems down the road. The motor is a NEMA B type motor.