I have feeder coming off of an 480V MCC out to a temporary power rack consisting of some heaters and two motors. The load I calculated was about 65A at 480V and a #2 so is being used as the feeder circuit. The contractor wants to use an HMCP breaker to protect the feeders out to this rack. From a previous fourmn I understood that an HMCP was only to be used with motors and would only provide short circuit protection (Even if the HMCP he wants to use is 100A). I told the contractor that we must use a thermal magnetic breaker in order to protect our feeder circuit from an overload condition since the magnetic breaker only provides short circuit protection and not overload protection. Am I correct with telling him to use a thermal magnetic breaker.
The breaker I had in mind for using is a Siemens HED4 breaker if anyone is familiar with it.