I have encountered an outdoor 1500-kVA step-down transformer, 13.8-kV delta to 0.48-kV wye. They are running the secondary conductors (535-kcmil DLO) in tray to an indoor 2000-A circuit breaker, which is part of an MCC assembly.
First, the wye-point of the secondary (neutral) is being run to a high-impedance resistor to keep the fault current to less than 5 amperes. The conductor is a 1/0 AWG DLO single conductor. The equipment bonding conductor is also 1/0 AWG DLO single conductor. Each phase is a square of 4 bundled 535-kcmil conductors spaced equally in a 6-inch fiberglass tray, 18 inches wide. The neutral is placed between the A-B phases and the EBC is placed between the B-C phases.
Q1. Aren't the phases supposed to be triplexed together (A-B-C) or squared together (A-B-C-N), and then paralleled to gain the necessary ampacity. They have it mounted and spaced as in a power-line configuration.
Q2. If the mounting is okay, how does one determine the spacing and placement of conductors?
Q3. One of the Engineers used Table 310.20 (single conductors in free air), 90-degree C column to justify the ampacity of these conductors. Doesn't 110.14(C)(1) limit the sizing to the 60 C and 75 C columns? I have only used Table 310.16 and I am not familiar with the useage of these other tables.
Q4. Are there heating issues involved where these conductors enter steel enclosures? All of these conductors pass through the indoor MCC steel enclosure wall via steel bushings and CG glands, and pass through the transformer enclosure through steel bushings (Myers hubs) and TMCX glands. They are arranged in an orderly manner, but they are as close together as the bushing will allow.
Thx
First, the wye-point of the secondary (neutral) is being run to a high-impedance resistor to keep the fault current to less than 5 amperes. The conductor is a 1/0 AWG DLO single conductor. The equipment bonding conductor is also 1/0 AWG DLO single conductor. Each phase is a square of 4 bundled 535-kcmil conductors spaced equally in a 6-inch fiberglass tray, 18 inches wide. The neutral is placed between the A-B phases and the EBC is placed between the B-C phases.
Q1. Aren't the phases supposed to be triplexed together (A-B-C) or squared together (A-B-C-N), and then paralleled to gain the necessary ampacity. They have it mounted and spaced as in a power-line configuration.
Q2. If the mounting is okay, how does one determine the spacing and placement of conductors?
Q3. One of the Engineers used Table 310.20 (single conductors in free air), 90-degree C column to justify the ampacity of these conductors. Doesn't 110.14(C)(1) limit the sizing to the 60 C and 75 C columns? I have only used Table 310.16 and I am not familiar with the useage of these other tables.
Q4. Are there heating issues involved where these conductors enter steel enclosures? All of these conductors pass through the indoor MCC steel enclosure wall via steel bushings and CG glands, and pass through the transformer enclosure through steel bushings (Myers hubs) and TMCX glands. They are arranged in an orderly manner, but they are as close together as the bushing will allow.
Thx