correct wiring for a residential 15kw heat strip

Bumpa

Member
Location
Jacksonville, Florida
Occupation
residential elctrician
I am connecting a 15kw heat strip for an air-conditioning unit. FLA 62.5, MCA 103.8a, MOCP 110a. Can I use a non-fuseable disconnect for the unit? I will use #4 copper thhn and an 80a 240v breaker at the panel.
 
The minimum circuit ampacity is 103.8 amps so the #4 is too small. #2 with a 110 amp OCPD will work
 