I would have two issues with your use of the GTD device to connect all lights in a corridor.
1. That doesn't provide the 2 required separate lighting systems - a normal system, and an emergency system. At least that's what I remember the code requiring. By putting all the lights on the emergency you have eliminated any "normal" system.
2. Only necessary, required egress lights can go on the emergency system. You can't just put all the lights on the emergency system. That gives a higher chance a ballast will short, or something will go wrong that will trip a branch breaker and shut off all the emergency lighting in one area.
Now, if you pick every 3rd light and put it on the GTD, I would be good with that.
Yeah that makes sense. If all the lights in the area were on the same branch, a short in one of the fixtures would black out the area. If it is in the emergency string, they obviously can't work.