I am working on an estimate for a kitchen remodel for 1920s house.
the service to the house was replaced about 15 years or so. found that water had been leaking into the panel for several years and causing oxidation on the busses and neutral along with rust on the load side branch breakers, main breaker and main breaker buss bar ties.
the load center is an outdoor 150AMP main breaker 20-30 space 240V with aluminum busses made by Siemens around 15 + years ago. Siemens has since changed the design of this panel and informed me there is no interior replacement for this panel, any altering of the panel by retro fitting a new interior would void the UL listing.
I informed the GC the panel would need to be replaced and there is not interior replacement available as he had hoped.
I also let the GC know I would not be willing to install new circuits and breakers especially with having to install arc fault breakers to the panel as they would fail over a short period of time
contractor is seeking another electrical opinion as he is not comfortable with my recommendations for replacing the entire panel
how would you as an inspector or engineer handle this situation. what would be your response to the GC to help him to understand why the panel busses could not be cleaned and new branch breakers along with new 150A main breaker with new bus bar ties or retro fitting a new interior be made.
Thanks.
Cameron
the service to the house was replaced about 15 years or so. found that water had been leaking into the panel for several years and causing oxidation on the busses and neutral along with rust on the load side branch breakers, main breaker and main breaker buss bar ties.
the load center is an outdoor 150AMP main breaker 20-30 space 240V with aluminum busses made by Siemens around 15 + years ago. Siemens has since changed the design of this panel and informed me there is no interior replacement for this panel, any altering of the panel by retro fitting a new interior would void the UL listing.
I informed the GC the panel would need to be replaced and there is not interior replacement available as he had hoped.
I also let the GC know I would not be willing to install new circuits and breakers especially with having to install arc fault breakers to the panel as they would fail over a short period of time
contractor is seeking another electrical opinion as he is not comfortable with my recommendations for replacing the entire panel
how would you as an inspector or engineer handle this situation. what would be your response to the GC to help him to understand why the panel busses could not be cleaned and new branch breakers along with new 150A main breaker with new bus bar ties or retro fitting a new interior be made.