Originally posted by mon6am:
DO you have to use any type of corrosion protection on AL conductors when connecting to breaker inside a multi family dwelling basement?
The code does not directly require the use of oxidation inhibitors. The only place the code even references oxidation inhibitors is here.Originally posted by mon6am:
The lugs on the breaker are rated for AL and CU so where in the code book dose it say I should use any type of corrosion protection.
Now this does not mean you are never required to use the oxidation inhibitors. The code still requires you to follow the labeling that comes with your equipment.110.14 Electrical Connections.
Because of different characteristics of dissimilar metals, devices such as pressure terminal or pressure splicing connectors and soldering lugs shall be identified for the material of the conductor and shall be properly installed and used. Conductors of dissimilar metals shall not be intermixed in a terminal or splicing connector where physical contact occurs between dissimilar conductors (such as copper and aluminum, copper and copper-clad aluminum, or aluminum and copper-clad aluminum), unless the device is identified for the purpose and conditions of use. Materials such as solder, fluxes, inhibitors, and compounds, where employed, shall be suitable for the use and shall be of a type that will not adversely affect the conductors, installation, or equipment.
It comes down to reading the label on the equipment, I can remember some GE disconnects switches that require oxidation inhibitors applied when AL is used on the terminations.110.3 Examination, Identification, Installation, and Use of Equipment.
(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.