Hi. I need a number of 240 3ph panels and 208/120 panels. Home Depot sells GE powermark panels TL30420C for $159 and TL42420C $167 with free shipping. These panels are also supposed to be rated for 240v 3 phase.
The price seems great, these same numbers sell for $500+ on other sites. I plan to use several of them as subpanels to power various single and 3 phase equipment. These panels also use the inexpensive THQL style breakers.
It would be nice to have a 300 or 400 amp panel, but the costs seem to be in the $800 to $1000 dollar range for these. I run out of load capacity on the panel way before I run out of spaces...
Are these panels a good deal? Are they unsuitable for light industrial use for any reason?
In one area I have a 240V 1ph coating oven with 60A requirement. Are commercial ovens non-continuous or continuous?
In this same area, I have two 50a 220v 1ph plugs for use with welders or other equipment. There is no dedicated equipment for these plugs.
In my 240V 200A 3ph panel, I have the 60A oven load, and the two 50A plugs = 160A
If oven is considered continuous, then the total is 75 + 100 = 175A
My panel is basically near capacity, even though the oven is the only load that will be used regularly.
Is this correct? I have to size for the 3 loads as above for the feeder circuit and panel capacity criteria?
Or is there some exception I don't know about...
I need a transformer to switch from the building 208Y120 power to 240v 3ph. I plan to supply several subpanels which will have both 1ph and 3ph branch circuits, using a main panel near the transformer. I need a 150kVA transformer, but a 300kVA is only a couple hundred dollars more... If I use an autotransformer.
https://canadatransformers.com/auto...-kva/primary:240-volt/secondary:208-volt.html
Is there any reason not to use the bigger transformer? It isn't much bigger (dimensions), either. I'd probably use a smaller than maximum OCPD and conductors, but could always upgrade them later for increased capacity. I would assume the amount of parasitic power is pretty much the same for any capacity transformer (no load current).
Also, I'm not sure if these transformers meet the latest energy code, or even if they have to in CT. I think the bigger unit would also last much longer, not being used near its rated capacity...
Any help on these questions would be most appreciated!
Thank you,
Bryan
The price seems great, these same numbers sell for $500+ on other sites. I plan to use several of them as subpanels to power various single and 3 phase equipment. These panels also use the inexpensive THQL style breakers.
It would be nice to have a 300 or 400 amp panel, but the costs seem to be in the $800 to $1000 dollar range for these. I run out of load capacity on the panel way before I run out of spaces...
Are these panels a good deal? Are they unsuitable for light industrial use for any reason?
In one area I have a 240V 1ph coating oven with 60A requirement. Are commercial ovens non-continuous or continuous?
In this same area, I have two 50a 220v 1ph plugs for use with welders or other equipment. There is no dedicated equipment for these plugs.
In my 240V 200A 3ph panel, I have the 60A oven load, and the two 50A plugs = 160A
If oven is considered continuous, then the total is 75 + 100 = 175A
My panel is basically near capacity, even though the oven is the only load that will be used regularly.
Is this correct? I have to size for the 3 loads as above for the feeder circuit and panel capacity criteria?
Or is there some exception I don't know about...
I need a transformer to switch from the building 208Y120 power to 240v 3ph. I plan to supply several subpanels which will have both 1ph and 3ph branch circuits, using a main panel near the transformer. I need a 150kVA transformer, but a 300kVA is only a couple hundred dollars more... If I use an autotransformer.
https://canadatransformers.com/auto...-kva/primary:240-volt/secondary:208-volt.html
Is there any reason not to use the bigger transformer? It isn't much bigger (dimensions), either. I'd probably use a smaller than maximum OCPD and conductors, but could always upgrade them later for increased capacity. I would assume the amount of parasitic power is pretty much the same for any capacity transformer (no load current).
Also, I'm not sure if these transformers meet the latest energy code, or even if they have to in CT. I think the bigger unit would also last much longer, not being used near its rated capacity...
Any help on these questions would be most appreciated!
Thank you,
Bryan