I have always wanted to see a Grizzly in the wild, but as in he is over theeeerrrrrre with me just a few steps more this direction.
You guys go first.
The problem with gensets running unloaded for long periods of time has to do with building up deposits in the engine, nothing to do with the generator portion other than the only way to put a load on a genset engine is to have a load on the generator. That's why some large standby gensets have "exercisers" that connect it to a load bank so they can simulate a load and prevent that deposit formation. On smaller ones it's usually easier to just run your load from the generator a couple times a year.
The myth on the unloaded motor vs counter emf issue is something I heard a long time ago too. I think it's a misinterpretation of basic motor theory. When a motor is first connected to a power source and it is not turning, the only thing restricting current flow is the wire resistance, which is so low that the initial inrush can be 10-20x the FLC and it that went on for more than a few cycles it would damage the motor. But the instant the motor starts turning, the counter emf begins to impede the flow. So I think someone misinterpreted "not moving" with "unloaded" and fostered that myth.
I have dealt with a lot of projects that used three-phase cage induction motors on centrifugal loads.This appears to happen with a centrifugal device like pump or blower driven by an induction motor.
But it won't run away under either conditions.
If you have to do that, it is a good candidate for a VSD.I have corrected many pumping application , that was tripping, by throttling the valve.
I have this discussion concerning irrigation pumps from time to time. It is counterintuitive,at first,I have corrected many pumping application , that was tripping, by throttling the valve. To many throttling appears to be increasing the load but its actually doing just the opposite.
During no-load running, its efficiency is very poor.Under these circumstances,I suspect that its temperature rating may be exceeded due to increased internal losses as a result of poor efficiency,if run at no-load for a long time.
Like?it will not overheat unless there are other issues.
Like?
What about the case of a genset. I have been told that a genset with no load on it is bad for it. Why is it better on the genset to run it with a load?
Besides being a total waste of money, a properly operating genset or motor will most likely run perfectly well without load. Why would you even want to?
With all the respect due, that's utter nonsense.During no-load running, its efficiency is very poor.Under these circumstances,I suspect that its temperature rating may be exceeded due to increased internal losses as a result of poor efficiency,if run at no-load for a long time.