18-19a Log #2197 NEC-P18 Final Action: Reject
(406.4(D)(1))
________________________________________________________________
Submitter: P. Bruce King, Stanley Consultants Inc.
Recommendation: Revise as follows:
(1) 2-pole, 3-wire, and 3-pole, 4-wire grounding, blade type receptacles shall
have the ground pin oriented on the top for vertical installations, and to the left
hand side for horizontal installations.
Substantiation: Reduce potential for fire in all types of buildings by reducing
or eliminating the possibility of objects falling onto the current carrying
conductor and grounded conductor, which could arc, thereby igniting
surrounding materials. The problem has been specifically identified in hospital
and residential settings.
Panel Meeting Action: Reject
Panel Statement: See panel action and statement on Proposal 18-21.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 10 Negative: 2
Explanation of Negative:
COSTELLO, P.: As this proposal continues to reappear there seems to be real
concern as to the direction the code would prefer for a safe installation. A Fine
Print Note would serve as a guide for most installations. With direction for the
safest use based on the outlets intended use, with general purpose outlets
configured with the ground, or grounded conductor in the up position unless
the stationary equipment served would be best served with a different
configuration based on the cord set and other location consideration.
WELLS, J.: I believe the substantiation, particularly that in Proposal 18-23, is
compelling. Our company, believing that where alternative installation choices
are available the safer alternative is preferred, stamped ?TOP? on some of our
receptacles oriented such that the ground was up. Where installers chose to
install it ground down, some inspectors, citing Section 110.3(B) forced the
contractors to rewire the receptacles with ground up. Regrettably, we were
forced to remove the marking.
18-21 Log #119 NEC-P18 Final Action: Reject
(406.4(G) (New) )
________________________________________________________________
Submitter: Gary Mayer, Jackson, MI
Recommendation: This is my proposal for the safe wiring and installation of
the standard 120 volt receptacle. Including Ground fault interrupter. I propose
that when installing the receptacle it be mounted with the ground terminal to be
in the up or top position. I have done it this way for many years now.
Substantiation: If a dead front plug is plugged into the receptacle that has a
heavy cord attached to it the weight of the cord will pull the plug down as
shown in photo #1 (if the receptacle is installed with the ground terminal in the
down position). When this happens, both terminals are exposed. In an industrial
or residential setting, this could lead to a dangerous situation. Someone could
accidentally come into contact with the energized side of the plug.
In photo #2, the same plug is in the receptacle, however the receptacle has
been changed to the ground in the up or top position. Now, even with the
weight of the cord pulling down it actually forces the terminals into the
receptacle. Now, there is no chance of anyone accidentially coming in contact
with the energized terminals.
I have seen may 220 volt dryer plugs wired with the ground terminal in the
down position and this is even more dangerous than the 120 volt receptacle.
The same as above also stands for the 220 volt receptacle. It should always be
installed with the ground terminal in the up or top position.
With that I will close. In the large scope of things it may seem quite small,
but I think it is something that has been overlooked for many years now and it
needs to be addressed. It may save someone from a painful shock, or worse. I
hope you will consider this suggestion and include it in the NEC.
Note: Supporting material is available for review at NFPA Headquarters.
Panel Meeting Action: Reject
Panel Statement: This proposal does not comply with the Regulations
Governing Committee Projects, Section 4-3.3, in that it does not contain
recommended text. See
www.nfpa.org.
The panel rejects the proposal that receptacles should be mounted with the
grounding contact in the up position for vertical installations or the grounded
circuit conductor slot in the up position for horizontal installations. The panel
has consistently rejected similar proposals and there is no ensurance that the
orientation of the receptacle will prevent the type of accident described in the
recommendation. The orientation of the grounding contact on the receptacle is
installation specific.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 10 Negative: 2
Explanation of Negative:
COSTELLO, P.: As this proposal continues to reappear there seems to be real
concern as to the direction the code would prefer for a safe installation. A FPN
would serve as a guide for most installations. With direction for the safest use
based on the outlets intended use, with general purpose outlets configured with
the ground, or grounded conductor in the up position unless the stationary
equipment served would be best served with a different configuration based on
the cord set and other location consideration.
WELLS, J.: I believe the substantiation, particularly that in Proposal 18-23, is
compelling. Our company, believing that where alternative installation choices
are available the safer alternative is preferred, stamped ?TOP? on some of our
receptacles oriented such that the ground was up. Where installers chose to
install it ground down, some inspectors, citing Section 110.3(B) forced the
contractors to rewire the receptacles with ground up. Regrettably, we were
forced to remove the marking.