Exactly.210.52(4) doesn not list a garage as one of the things that can seperate a countertop space.
Then show code to back up you call.Originally posted by jbwhite:
edit... i think it is a judgement call weather or not 13 inch counter will be used as counter space. i think it will.
The receptacles are installed in the wall as the code states in wall space.210.52(C)(1) Wall Counter Spaces. A receptacle outlet shall be installed at each wall counter space that is 300 mm (12 in.) or wider.
so now we have a counter top space wider than 24 inches. .... in this case it just happens to be infront of a garage...... so it need to have recs.Originally posted by websparky:
The spacing of the receptacles is independent of the garage. If the garage has a receptacle in it or not, the space is not considered nor is the receptacle counted as one of the required countertop ones.
(5) Receptacle Outlet Location. Receptacle outlets shallOriginally posted by jwelectric:
This is not allowed to be done in the cabinet in front of an appliance garage nor are we allowed to install a receptacle in the face-up position.
So now just how do you intend on installing this receptacle?
No, read what I said again. The garage's placement does not effect the outlet placement, therefore there isn't a space wider than 24".so now we have a counter top space wider than 24 inches. .... in this case it just happens to be infront of a garage...... so it need to have recs.
Why did you leave out the rest of the section that would told you how to install 12 inches below the countertop?Originally posted by jbwhite:
be located above, but not more than 500 mm (20 in.) above,
the countertop. Receptacle outlets rendered not readily accessible
by appliances fastened in place, appliance garages,
sinks, or rangetops as covered in 210.52(C)(1), Exception,
or appliances occupying dedicated space shall not be considered
as these required outlets.
Exception to (5): To comply with the conditions specified in
(1) or (2), receptacle outlets shall be permitted to be
mounted not more than 300 mm (12 in.) below the countertop.
Receptacles mounted below a countertop in accordance
with this exception shall not be located where the
countertop extends more than 150 mm (6 in.) beyond its
support base.
You can't just start installing receptacles anywhere 12 inches below the countertop that you decide would be a good place to install one. You need to read the whole section.(1) Construction for the physically impaired
(2) On island and peninsular countertops where the countertop is flat across its entire surface (no backsplashes, dividers, etc.) and there are no means to mount a receptacle within 500 mm (20 in.) above the countertop, such as an overhead cabinet