So (2017) 210.12 on AFCI refers to "kitchens, family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, laundry areas, or similar rooms or areas"
And (2017) 210.52(A) on wall space receptacles refers to "kitchen, family room, dining room, living room, parlor, library, den, sunroom, bedroom,
recreation room, or similar room or area"
The difference is the omission of "closets, hallways, laundry areas" from 210.52(A). So if a "pantry" is a similar area for 210.12 purposes, is a "pantry" a similar area for 210.52(A) purposes? I.e. is the pantry similar to a "kitchen" (wall space receptacles required) or similar to a "closet, hallway, laundry area" (wall space receptacles not required)?
Cheers, Wayne
P.S. This reminds me that since the 2017 NEC, wall space receptacles in kitchens have been required along walls with countertops, which receptacles must be in addition to the countertop receptacles. Something everyone overlooks and probably wasn't intended.