brother
Senior Member
Well i ran into another 'i dont derate, and im gonna stuff this pipe as much as i can' project left by someone else.
I know some people dont derate, but i wanted to be sure i was counting the wires right. This a 3 phase 4 wire Y system, 120/208. there are 12 ccc in this pipe as i originally counted. Aparrently they ran 2 full boats and then added 2 more circuits with its neutral (2 hots and 2 neutrals). It also had the 2 pole 208 (black and red) circuit as well.
I wanted to be sure that counting the 2 pole 20 amp 208 (phase to phase) there, is correct?? Even though those phase cancel each other. I do count them in the current carrying scheme right? its late, just double checking myself.
Also the people that previous installed these never derated anything, so there are still on the 20 amp breakers with #12. So far no melt downs though. I reread 310.15 (4)(a) Neutral Conductor and started second guessing myself, i do still count all the neutrals right??
I know some people dont derate, but i wanted to be sure i was counting the wires right. This a 3 phase 4 wire Y system, 120/208. there are 12 ccc in this pipe as i originally counted. Aparrently they ran 2 full boats and then added 2 more circuits with its neutral (2 hots and 2 neutrals). It also had the 2 pole 208 (black and red) circuit as well.
I wanted to be sure that counting the 2 pole 20 amp 208 (phase to phase) there, is correct?? Even though those phase cancel each other. I do count them in the current carrying scheme right? its late, just double checking myself.
Also the people that previous installed these never derated anything, so there are still on the 20 amp breakers with #12. So far no melt downs though. I reread 310.15 (4)(a) Neutral Conductor and started second guessing myself, i do still count all the neutrals right??