ceb58
Senior Member
- Location
- Raeford, NC
Per 225.32 either outside or immediately inside UNLESS you can apply 700.12(B)(6) (many generators do not have "service rated" breakers)
Plus it must comply with 445.18
Per 225.32 either outside or immediately inside UNLESS you can apply 700.12(B)(6) (many generators do not have "service rated" breakers)
VI. Service Equipment ? Disconnecting Means
230.70 General. Means shall be provided to disconnect all
conductors in a building or other structure from the serviceentrance
conductors.
Originally Posted by roger The meter and service disconnect must be mounted on some sort of structure even if it's simply a pole for the service.
VI. Service Equipment ? Disconnecting Means
230.70 General. Means shall be provided to disconnect all
conductors in a building or other structure from the serviceentrance
conductors.
So if the building has a metal water main and your service is 100+ feet away do you still use it as an electrode? If so that means you are running a GEC and a EGC?
I wonder if the CMP though of this.
250.50 Grounding Electrode System. All grounding electrodes
as described in 250.52(A)(1) through (A)(7) that are
present at each building or structure served shall be bondedQUOTE]
see the "Each in red above"
Again in 250.32 Two or More Buildings or Structures Supplied from a Common Service:
the grounding electrode(s) required in Part III of this article at each building or structure
someone please tell me what conductors are inside a pole???
Where is a disconnect required for conductors "outside a pole"???
the requirement for grounding electrodes is for each individual building, not all the buildings, so no GEC needed between buildings or structures.
250.50 Grounding Electrode System. All grounding electrodes
as described in 250.52(A)(1) through (A)(7) that are
present at each building or structure served shall be bondedQUOTE]
see the "Each in red above"
Again in 250.32 Two or More Buildings or Structures Supplied from a Common Service:
I understand the wording of the code.
My point was the requirement to bond the neutral and ground the service at a pedestal or pole does not really make sense to me, when the laterals are completely outside the building.
It would seem to make more sense to to count those conductors as service and ground the neutral at the building. The only electrodes to are going to be able to hit are a couple of rods. It would seem to be a better system to have your electrodes and neutral bond closer to the OCP devices because we know that most made electrodes are not worth a crap when it comes to opening the OCP on a phase/ ground fault.
The question is why did the op put a disconnect at the pole? Since one is needed at the dwelling either outside or directly inside as near as possible to the entrance of the conductors then a disco is not necessary at the pole. Set the meter and run three wires to the house.
My questions is in regard to the what I would call a "country residential service". It is a pretty typical service that we have installed numerous times. There is a meter socket / main breaker / and ground rods out by the road. There is then a feeder going from this point to the home +/- 100' away. This feeder goes into the home to a "sub panel".
The question is why did the op put a disconnect at the pole?