Couplings/Unions in Class 1 Div 2 Areas

Status
Not open for further replies.

rcwilson

Senior Member
Location
Redmond, WA
Contractor installed a security system in a gas compressor room running wiring in rigid conduit. Room is classified as Class 1 Div 2. These circuits are low voltage (power over ethernet) but not intrinsically safe. Conduit is appropriately sealed at Class 1 Div 2 to non-hazardous boundary. Equipment is all Class 1 Div 2 rated.

Some conduit runs are assembled with the C-H "HDG" 3-piece, concrete tight couplings that connect conduit without turning, like a union. These couplings are not listed in the catalogs as Class 1 Div 2. Some electricians on site are saying all the HDG couplings need to be replaced with explosion proof unions.

Contractor is quoting 501.10 B (4) "Boxes and fittings shall not be required to be explosion proof..." Per definitions, a coupling is a fitting.

Are these couplings suitable for this application? (I tried to find UL file E-19189 for the HDG coupling but haven't located it yet.)
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
In general, there is no need to use explosionproof conduit fittings and unions in Class I, Division 2 applications. The execption would be fittings and unions that are installed between an enclosure that requires a seal and the seal.
I am not sure why there is even a listing for boxes and fittings for use in Division 2 areas, as nothing special is required. I expect the listing is just for marketing purposes to sell more expensive boxes and fitting.
 

rcwilson

Senior Member
Location
Redmond, WA
Thank you, that is what we thought. We figured if a standard LB fitting is ok, why not a UL listed coupling?

I appreciate the confirmation. We did verify there is nothing but solid conduit between the seals and enclosures or the boundary.
 