800.154 Applications of Listed Communications Wires and Cables and Communications Raceways. 
Communications wires and cables shall comply with the requirements of 
800.154(A) through 
800.154(F) or where cable substitutions are made in accordance with 
800.154(G) 
(A) Plenum. Cables installed in ducts, plenums, and other spaces used for environmental air shall be Type CMP. Abandoned cables shall not be permitted to remain. Types CMP, CMR, CMG, CM, and CMX and communications wire installed in compliance with 
300.22 shall be permitted. Listed plenum communications raceways shall be permitted to be installed in ducts and plenums as described in 
300.22(B) and in other spaces used for environmental air as described in 
300.22(C). Only Type CMP cable shall be permitted to be installed in raceways.