Here is a problem I've been having with a compressor in my shop. The unit came with a 15 amp plug and in the literature that came with it, it states that it should be connected to an individual 15 ampere circuit. So I installed an individual 15 amp circuit with #12 AWG THHN. The problem is that it trips the 15 ampere circuit on start up. So I installed a 20 amp circuit breaker with a single 20 amp receptacle, plugged in the compressor and it now trips only sporadically (usually when I'm wedged under my truck with an air ratchet).
To correct the problem I thought about installing a 25 or 30 amp circuit breaker, but now that creates a problem because the receptacle is rated for 20 amps and someone could unplug it and use the receptacle for something else which is protected by a 25 or 30 amp breaker. I've also considered hardwiring the unit to eliminate the receptacle issue altogether but then I would lose the portability of the compressor. Any thoughts?
To correct the problem I thought about installing a 25 or 30 amp circuit breaker, but now that creates a problem because the receptacle is rated for 20 amps and someone could unplug it and use the receptacle for something else which is protected by a 25 or 30 amp breaker. I've also considered hardwiring the unit to eliminate the receptacle issue altogether but then I would lose the portability of the compressor. Any thoughts?