Nice, clean crawl space!
Is there a main disconnect at the meter?
Would seem to be 'easy' to run a 4th conductor down the duct in the crawl space and install a disconnect at the meter.
And some more questions:
What's the orange 'pipe' running off from behind the meter.Looks like a hose bib to the left of the conduits.
Is that an extension cord coiled up in there? No that looks like the cable company underground wiring which is run in the orange inner duct.
What's that other pipe in between the conduits to the meter housing? Maybe for the GEC to the ground rods?
And what's strapped to one of the conduits into the meter housing? CATV?
Would seem to be 'easy' to run a 4th conductor down the duct in the crawl space and install a disconnect at the meter.
And some more questions:
What's the orange 'pipe' running off from behind the meter.Looks like a hose bib to the left of the conduits.
Is that an extension cord coiled up in there?
What's that other pipe in between the conduits to the meter housing?
And what's strapped to one of the conduits into the meter housing?
Wonder why they didn’t run SER and secure it to the bottom of the joist
Sent from my iPhone using Tapatalk
It would still have been an excessive length of service conductors inside the building. Possibly the installer thought that it would be OK if run in conduit. (It's not.,..)
The NEC language, "nearest the point of entry" indeed does not set a hard limit, leaving it up to local AHJs to interpret either by setting their own measurements or normalizing a more flexible case by case judgement. But I doubt that any jurisdiction, when asked, would say that the OP's example is compliant.
Come on guys.
All I've heard in the previous 15 posts is disconnect,disconnect, disconnect, disconnect, disconnect.....
You could install Umpteen disconnects between the meter and the service panel in this scenario and you'd still be no better off unless you installed some type of OCPD at the beginning.
JAP>
230.91 Location. The service overcurrent device shall be an
integral part of the service disconnecting means or shall be
located immediately adjacent thereto. Where fuses are used as
the service overcurrent device, the disconnecting means shall
be located ahead of the supply side of the fuses.
I said a service disconnect which is required to have an OCPD in or adjacent to it so it should be understood that it will have overcurrent protection. I would assume that the others meant the same.![]()