Guys, I did a service change on a home built in 1925 last Thursday. I get a call on Tuesday that a light bulb is burning out. I find out this condition is because the light has 240v when 1 of the the?3ways is up. When it is down I have 120v on the shell of the light fixture. I was having a very hard time figuring out what the heck was happening and what it had to do with a panel change, if anything. After about 2 and 1/2 hours I figured this out, Both the 3ways have 120v across the traveler terminals and a single wire that goes to the light on the common, the 120v feed is on different circuits. The light functions like a normal 3way as long as the circuits are on the same phase. I don't know how to put drawings on here so draw it out yourself if you wish. Depending on the position of the 3way you have at the light one of these combinations 2 neutrals (off) 2 hots same phase (off) or 1 hot 1 neutral with polarity flip flopping. I put the circuits on the same phase as it worked as it did before. Hope I explained this ok. Has anyone ever seen this, I can think of a few hazards with this set up, I would like to know what hazards you guys can think of with this set-up and lastly what would you tell the homeowner?
Thanks in advance