I stumbled across this and just had to share. I've never seen anything this messed up in my entire life.
Dang nabbit!Ring circuits!
Single voltage with neutral by the looks of it. No MWBC.I thought the UK used single-ended, single-voltage services that don't have a "neutral" wire?
Yeah, this part confused me somewhat. I think you must be correct that the breaker for the downstairs receptacle circuit disconnected the neutral, because otherwise I didn't see how the neutral on the boiler plug became energized to ground without being a straight short circuit with both circuits turned on. My best theory is that with the boiler circuit energized, the appliance passed the voltage (almost?) straight through to the neutral on the plug, thus energizing the disconnected neutral wire. All in all, somewhat similar to how here in the states you'd have voltage from a disconnected neutral wire to ground if you lift one line and neutral of an MWBC while the other line is still energized and load turned on.For those interested in the discussion who don't like videos, the upshot, per the narrator, is this:
...
2) In the system state where the electrician was shocked, his meter on the receptacle circuit read voltage L-G and N-G, but not L-N. I would expect it to have read normally. But perhaps since the breakers are RCD, they actually disconnect the neutral conductor when off. In which case the raised N-G voltage would have been due to capacitive coupling with the energized L conductor?
...
I think he may have been seeing 170 as the result of static (always on/plugged in or capacitive) loads on the two dircuits. One circuit energized the neutral but loads on the "open" circuit bled off some of the voltage. But capacitive loads could not have supported much current.Yeah, this part confused me somewhat. I think you must be correct that the breaker for the downstairs receptacle circuit disconnected the neutral, because otherwise I didn't see how the neutral on the boiler plug became energized to ground without being a straight short circuit with both circuits turned on. My best theory is that with the boiler circuit energized, the appliance passed the voltage (almost?) straight through to the neutral on the plug, thus energizing the disconnected neutral wire. All in all, somewhat similar to how here in the states you'd have voltage from a disconnected neutral wire to ground if you lift one line and neutral of an MWBC while the other line is still energized and load turned on.
Also not sure I can explain why the voltage was 170, not 230, and why it went up when other items were unplugged. Not that I've tried to puzzle it out completely. (Neither did our hero in the video, apparently.)
A replacement boiler (probably with some fancier electronics) needed both constant power and switched power. So the installer of that boiler grabbed constant power from a nearby receptacle circuit that was on a different breaker. They used L-N from the receptacle circuit and only switched power from the original circuit.
A previous electric boiler (to heat water for domestic use and for space heating) was supplied with a 2-wire circuit that only had switched power from a thermostat/controller. A replacement boiler (probably with some fancier electronics) needed both constant power and switched power. So the installer of that boiler grabbed constant power from a nearby receptacle circuit that was on a different breaker. They used L-N from the receptacle circuit and only switched power from the original circuit.
The result was that when just the receptacle circuit was shut off, but the controller called for heat, the boiler circuit backfed the receptacle circuit line conductor and shocked the electrician.
Ah, right, I failed to realize that since the RCD wasn't tripping during normal usage conditions, that implies that all the power to the heating element was coming from the constant power circuit, as that is the only circuit whose neutral was in use.With electronic controls the current drawn on the switched power coming from the thermostat controller might be quite low, and perhaps significantly less that the 30mA needed to trip an RCD.
What the heck kind of boiler is that? I rest my case.
-HalA previous electric boiler (to heat water for domestic use and for space heating) was supplied with a 2-wire circuit that only had switched power from a thermostat/controller. A replacement boiler (probably with some fancier electronics) needed both constant power and switched power. So the installer of that boiler grabbed constant power from a nearby receptacle circuit that was on a different breaker. They used L-N from the receptacle circuit and only switched power from the original circuit.
Seem's that's how it's designed. The guys who bolloxed it up miswired it, right?My point is a boiler needing two sources of power is just asking for trouble. The control voltage should have come from the boiler itself, not a separate circuit.
-Hal
Seem's that's how it's designed. The guys who bolloxed it up miswired it, right?
It does seem weird to use line voltage for a control circuit though.