Zcon
New User
- Location
- Northern Minnesota
Discovered through actual problem and damage that UPS systems are not protected for ground faults properly. Reason most UPS units go into overload on a ground fault at 1/4 of a cycle and the branch circuits they serve are protected by molded case circuit breakers mounted in UPS panels. These breakers trip at 1/2 cycle so a small ground fault on a branch circuit can put all connected loads in danger off dropping out. The fix is special UPS fuses or panels fuses are put in series with the connected loads on the branch circuits. I suspect that many UPS panels are installed this way the panels were installed in my case by contractors in 2006 then about 2010 because of no anti short bushings in a underground pull box a ground fault occurred on a 30 amp double pole sub feed breaker. The ground fault caused the whole new UPS to trip out losing all UPS panel loads at the same time the way it looks to a layman being called out in the middle of the night is everything down with no trips on the molded case breakers and a overload alarm on the UPS serving them all. The UPS was checked out for damage after ohm meter checks were done on the branch circuits the panels that were clear were reenergized the faulty circuit was locked out for safety. In this case severe damage was done to equipment and people came close to being hurt the new control system that the new UPS was serving went completely dead everything quit including redundant power supplies and controllers with no way to control anything and no critical indication of the plant equipment status available all fail mode logic that was programmed in the valve slaves did not work. There is some talk of UPS coordination requirement now on the web but very little in 2010 and I thought the industry would have put out a mandate to repair all systems installed this way but it has not happened these systems are time bombs waiting to happen but nothing is being done. So I went to a code update class and asked if anybody knew about this and nobody did the word is not getting where it needs to be.
Zcon
Zcon