Critique my diagram.

Status
Not open for further replies.
Why use a contactor for the fans? If they can share a single circuit (i.e., 120v and <20a), the micro's, usually rated at 16a, can handle the current. After all, the micro carries the exhaust-fan's current during system trip in your drawing.

Because I can charge more - LOL - Plus I usually price the job unseen and I price the contactor just in case it's needed. I don't usually know what fans they are putting in (used or new) or what voltages they are going to be. Our micro's are rated 22A.

Notice that the horn/strobe is connected between the two blowers; the current required is miniscule. A gas-valve and its reset box would be connected across the intake fan (or its contactor) along with the appliance/receptacle contactor(s).

Sorry, but I'm not so sure about the HS working that way, I understand what your saying but I would want a clean neutral for the HS.

About the sensors mentioned: when they install systems here, the Ansul head has two cables, one for manual pulls, and the other under tension. There are lead links in the cable above the grease-catchers.

The sensor I am talking about is electric (http://www.vulcanco.com/calstat.html) not the fusible links.
 
dmanda24 said:
so there is current going trough the intake fan just not enough to make it move? how about the contactor coil, it is also connected in series with the strobe, would it be enough current to energize the coil?
Not in my experience. I don't use small control relays, but contactors such as Square D's 8910DPA13V02 (120v). I tried to find data on coil current, but couldn't.

The horn/strobe the fire guys leave for me says the max current is 150 ma. I'd have to connect a horn/strobe and a contactor coil in series and measure the voltages.
 
dmanda24 said:
Larry??????
What?????! :grin: Hey, I was out installing contactors today. Gimme a break.

Actually, we did a supression system today, and I used two of those contactors in parallel for appliances. However, the second micro was available, so I didn't have to 'cheat.'
 
How would you wire an exhaust fan and a strobe using only one micro, I had to install a contactor.

Edit. Note, there is no intake fan.
 
dmanda24 said:
How would you wire an exhaust fan and a strobe using only one micro, I had to install a contactor.

Edit. Note, there is no intake fan.
Hood lights? Appliances or receptacles?
 
dmanda24 said:
LarryFine said:
dmanda24 said:
How would you wire an exhaust fan and a strobe using only one micro, I had to install a contactor.

Edit. Note, there is no intake fan.
Hood lights? Appliances or receptacles?
None, it was a small kitchen hood.
In that case, you need a contactor.

Unless you're willing to leave the exhaust running 24/7.
 