At some point - someone had posted a table the cross-sectional area of common cables to include 14-2 and 12-2 NM related to conduit fill.

Anyone know them off the top of thier head?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Not sure where that info came from but I remember that you're to consider the flat cable to be round to find it's diameter.
 

mdshunk

Senior Member
Location
Right here.
e57 said:
Anyone know them off the top of thier head?
Yeah! :grin:

14-2 NMB .1018
12-2 NMB .1320
10-2 NMB .1917
8-2 NMB .2942
6-2 NMB .3664
14-3 NMB .0740
12-3 NMB .0946
10-3 NMB .1399
8-3 NMB .2507
6-3 NMB .3318
14-2 UF .1405
12-2 UF .1684
10-2 UF .2107
8-2 UF .3610
6-2 UF .4657
14-3 UF .2651
12-3 UF .3078
10-3 UF .4151
8-3 UF .8808
6-3 UF 1.1747

Just a few... off the top of my head. :wink:
 

mdshunk

Senior Member
Location
Right here.
infinity said:
Not sure where that info came from but I remember that you're to consider the flat cable to be round to find it's diameter.
True. The list I just gave is the major dimension of the elipse, where applicable.
 