buffalonymann
Senior Member
- Location
- NC
Question: I have crydom SSRs in my facility - I see in the specs turn on voltage is 90VAC and turn off voltage is 10VAC. Would like to gain better understanding of exactly what is happening to turn these off.
Question: I have crydom SSRs in my facility - I see in the specs turn on voltage is 90VAC and turn off voltage is 10VAC. Would like to gain better understanding of exactly what is happening to turn these off.
It means that your control signal (the equivalent of a “coil”) must be a minimum of 90VAC, and if in the “off” state there is more than 10VAC on the signal, ie “leakage” in solid state control devices, it may not turn off.
No, 10V is what’s referred to as the “must turn off” voltage, meaning if it is more than 10V, it might not turn off.You may have meant "less".
BTW, these are min and max numbers. There is no real way to tell on a specific relay where it will operate. However the spec is telling you if the input control voltage is less than 10 V it won't turn on, and if it is greater than 90 V it will. Between those points it is hard to tell what will happen.
It means that your control signal (the equivalent of a “coil”) must be a minimum of 90VAC, and if in the “off” state there is more than 10VAC on the signal, ie “leakage” in solid state control devices, it may not turn off.
:thumbsup:
Mechanical relays have an unavoidable hysteresis because of the moving armature. Solid state relays will generally design in similar hysteresis, even when it is not an inherent feature of the gate elements themselves.
I am saying that some solid state relay designs could easily be made without hysteresis, but it is designed in anyway.Not sure what your saying in the latter half of your comment
I am saying that some solid state relay designs could easily be made without hysteresis, but it is designed in anyway.
Other designs, like the Triac circuitry in a two wire dimmer, cannot avoid hysteresis.
Sent from my XT1585 using Tapatalk
I can not give you an answer without actual measurements in your circuit. This at least mean some scope measurements.I want you guys to think about this, when we do turn off the control voltage there remains an induced voltage of about 18VAC on the control circuit. The SSR does stop conducting full current, but we see high leakage voltage at the output. When we drive that 18VAC down to 7VAC, we see the leakage voltage disappear.
If you remove the wires to the control terminals, then do you still see 18 V across the terminals? I doubt that you wiil. If that voltage goes away, then the origin of the voltage is from your control circuit. 18 V to the SSR input terminals may be sufficient to cause current flow thru the SSR output area.I want you guys to think about this, when we do turn off the control voltage there remains an induced voltage of about 18VAC on the control circuit. The SSR does stop conducting full current, but we see high leakage voltage at the output. When we drive that 18VAC down to 7VAC, we see the leakage voltage disappear.
Almost certainly if your three phase Crydom SSR is driven directly from a PLC AC output, then you may have sufficiently high leakage current to produce the 18 V.I'm in total agreement that the control voltage is external. I'm trying to get a handle on what is happening in the circuit - let me give you a bigger picture. We're using these SSRs in our extrusion process, a PLC receives a signal from a thermocouple and pulses the SSR via an AC output module to energize resistance heaters. I suspect my AC output module is leaking current when the node is off and this is where the 19 VAC comes from. I have been told by a tech that there is about 190 volts across l1 and l2 output when the control circuit is turned off. Furthermore I am told when they disconnect the control voltage the 190 VAC goes away
181024-1518 EDT
buffalonymann:
Almost certainly if your three phase Crydom SSR is driven directly from a PLC AC output, then you may have sufficiently high leakage current to produce the 18 V.
You are referring to the PLC output module leaking sufficient current? This is what I think is happening as well.
I don't know what l1, l2 are (L1, L2), but I suspect these are some lines, but where?
Yes - L1 and L2 output on the SSR
Shunt the input of your SSR with 5000 ohms 5 W, and see if this lowers the 18 V sufficiently. If not go to a 1000 ohm 20 W which should be more than adequate, just wastes power. A better solution is to use a relay output on the PLC.
I've contemplated a resistor across the control input; my first response is to correct the problem if it can be at a reasonable cost. This system, once heated, also maintains the temp so the output cycles on and off about every second or two, which is probably why they didn't design it with relay output on the PLC module
Since I don't know what L1 and L2 are the 190 V does not mean much, but I expect that these might be a load resistance, part of your heater. Are L1 and L2 two wires to a three phase delta heater?
The heaters I've looked at are single phase. I inherited this issue, not sure if the orginal design was meant to be three-phase delta heaters; that's another issue I need to review.
.
FWIW, I have had something similar before. In my case it was a PLC with triac outputs trying to energize a motor starter coils. This particular motor starter required an input reference voltage for the control circuit. The triac output was about 1.5 volts lower (IIRC) and that wasn't close enough to let motor starter pull in.
I could have made a voltage divider with a pair of resistors to lower input reference the required 1.5 volts. Instead I wired the PLC to an interposing relay's coil and wired reference voltage to common and motor starter coil to N.O. contact. Added plus was said relay had push to test feature and LED to let me know if PLC was calling for MS to be pulled in. Also went this way because I had previous problems with PLC outputs not coping well with inductive loads and needing snubbers across them.
Might be worth the trouble for you. Lets you push a tab on the relay and verify MS and heater are working without PLC command. Lets you see (from relay LED) if PLC is outputting a command when you feel it should.
The Crydom drawing shows one output switch terminal pair as A1-A2, another as B1-B2, and the third as C1-C2. I don't believe any one of these pairs is your L1-L2.I don't know what l1, l2 are (L1, L2), but I suspect these are some lines, but where?
Yes - L1 and L2 output on the SSR