Almost certainly if your three phase Crydom SSR is driven directly from a PLC AC output, then you may have sufficiently high leakage current to produce the 18 V.
You are referring to the PLC output module leaking sufficient current? This is what I think is happening as well.
I don't know what l1, l2 are (L1, L2), but I suspect these are some lines, but where?
Yes - L1 and L2 output on the SSR
Shunt the input of your SSR with 5000 ohms 5 W, and see if this lowers the 18 V sufficiently. If not go to a 1000 ohm 20 W which should be more than adequate, just wastes power. A better solution is to use a relay output on the PLC.
I've contemplated a resistor across the control input; my first response is to correct the problem if it can be at a reasonable cost. This system, once heated, also maintains the temp so the output cycles on and off about every second or two, which is probably why they didn't design it with relay output on the PLC module
Since I don't know what L1 and L2 are the 190 V does not mean much, but I expect that these might be a load resistance, part of your heater. Are L1 and L2 two wires to a three phase delta heater?
The heaters I've looked at are single phase. I inherited this issue, not sure if the orginal design was meant to be three-phase delta heaters; that's another issue I need to review.
.